Neutral-to-Ground Bonding: One Place Only

페이지 정보

profile_image
작성자 Elsie Lemus
댓글 0건 조회 8회 작성일 26-09-14 18:41

본문

In a correctly built system the neutral and the grounding conductors are joined at exactly one point, and that point is the main service disconnect. Everywhere downstream of it they must stay completely separate. This single rule explains a surprising number of the problems found in older panels and in subpanels added by amateurs.



The reason for joining them at all is fault clearing. When a hot conductor touches a grounded metal case, the current needs a low-impedance path back to the source so that a very large current flows and the breaker opens immediately. The bond at the service is what completes that path.



The reason for joining them only once is that both conductors run alongside each other back to the panel. If they are also connected at a second point, current returning from normal loads will divide between them, and the grounding conductor starts carrying working current. That is not what it is for. It means metal enclosures, appliance cases, water pipes and anything else bonded to the system now have a small voltage on them under load, and if the neutral ever opens somewhere upstream, that small voltage becomes the full supply voltage.



In a subpanel the correct arrangement is four conductors from the main panel, two hots, a neutral and a separate grounding conductor. Inside the subpanel the neutral bar is isolated from the enclosure, usually by removing a bonding screw or strap, and the grounding conductors land on their own bar bolted to the metal.



The common error is a three-wire feed to a subpanel with the neutral bar left bonded, which was permitted in some older installations for detached buildings and is not permitted now.



Detached structures deserve extra attention because the ground rod at the outbuilding does not replace the grounding conductor from the house. Earth is a poor conductor and will not carry enough current to trip a breaker. The wire is what does that work.



A quick way to check an existing subpanel is to look at the bars. If neutrals and grounds are landed together on one bar bolted straight to the enclosure, and only three conductors arrive from the main panel, that panel is bonded where it should not be. Correcting it means adding an isolated bar and, in most cases, pulling a fourth conductor.



Background reading: aryba.kg

댓글목록

등록된 댓글이 없습니다.

회원로그인

회원가입

사이트 정보

회사명 : 회사명 / 대표 : 대표자명
주소 : OO도 OO시 OO구 OO동 123-45
사업자 등록번호 : 123-45-67890
전화 : 02-123-4567 팩스 : 02-123-4568
통신판매업신고번호 : 제 OO구 - 123호
개인정보관리책임자 : 정보책임자명

접속자집계

오늘
1,575
어제
2,162
최대
2,388
전체
72,384
Copyright © 소유하신 도메인. All rights reserved.